69kv Power Line Glowing

Last post 07-01-2009, 5:41 PM by Bill. 4 replies.
Sort Posts: Previous Next
  •  06-29-2009, 8:16 AM 3193

    69kv Power Line Glowing

    Attachment: powerline.bmp

    Last month, in the early morning hours, I embarked on the exciting scheduled task of Inspecting the miles of power lines that are strung throughout the Chemical Plant in Central Florida were I work as a Reliability Analyst. The task was simple. I was to perform an Infrared and Ultra Sound inspection on the high voltage power line connections, disconnects, fuses, transformers as well as the electrical equipment and components located in nine substations through out the facility.

     

    I started on the south-east side of the plant and worked my way north-west toward the two Steam Turbine Generators that were supplying several plants as well as the public power grid with an approximate combined load of 59 mega watts at 69kv that morning. I found several small problems working my way around including a few high voltage components with corona activity present that I observed and recorded with the Ultrasound equipment as well as a faulty connection at a fuse clip on a high voltage line supplying power to a Processing Plant that I observed and captured with an infrared camera.

     

    Then I saw something strange, with my own naked eyes. Just two power poles away from the first turbine was a bright red line above my head. At approximately 5:30AM I found myself in the dark spinning in a circle looking up, down and all around visually trying to figure out where the reflection was coming from. Then it hit me! It wasn't a reflection. I could visually see the 69kv power line glowing bright red in the dark.  Stepping back away from the pole, I viewed it on the IR camera from what I felt was a relatively save distance and angle, just incase the line decided to break and fall in my presence.

     

     On the center phase jumper, I observed a pretty apparent inaccurate temperature of approximately 312°F due to being out of my measurable field of view with a Delta T of 228°F and another anomaly that was not seen visually with an inaccurate temperature of approximately 137°F with a Delta T of 57°F on the lower phase. Undeterred by the inaccurate measurements I still saved the image. At the time I believed that the temperature of the center phase jumper must have been at least 800°F in order for it to produce the bright red glow that was visually present. I also snapped a visual picture in an attempt to capture an image of the line glowing in the dark. I immediately informed the Production Manager in charge of the turbines and escorted him to the pole so he could see for himself that it was glowing. After his visual conformation he informed his superiors immediately of the situation at hand.

     

    With in a few hours of discovering the fault, Plant Reliability Engineers, Maintenance Planners and the Plant Electrical Superintendent had a plan in place to perform an unscheduled power outage and repair the connections immediately in an effort to avoid the additional cost that would be incurred if the plants were to shut down abruptly with out any notice at all.

     

     The power line that was isolated was leaving one of the steam driven turbines carrying a load of approximately 34mw at 69kv when the fault was discovered. It supplied power to the local power companies grid as well as six different Processing Plants, Administrative Offices and one Maintenance Shop that where all shut down unscheduled but with enough notice to reduce any additional cost of corrective measures that would have needed to take place had the plants gone down without the proper procedures and protocols being followed.

     

    Upon shut down the High Voltage Electricians discovered the connections on the jumper that had been glowing were so damaged that the entire line length had to be replaced from one pole to the other. The initial investigation indicated an improper compression connecter was used to splice the jumper to the line going to the next pole. The connector was sized for the gauge of wire used between the two poles, however the jumper was of a smaller gauge thus for making a weak connection which was headed for catastrophic failure.  

     

     The faults were reassessed the following morning after the proper corrective measures were taken. The Delta T on both faults was reduced to within 5°F under approximately the same load, ambient and surrounding conditions.

     

     



    Justin Ardekani
    PdM - Reliability Analyst
    ASNT NDT Level II IR Thermographer
    IACW UST Level I Ultrasound Inspector
    The Snell Group
    www.thesnellgroup.com
  •  06-29-2009, 9:19 PM 3195 in reply to 3193

    Re: 69kv Power Line Glowing

    Wow! Talk about Homeland Security.
    Thermally Yours,

    John
    ASNT NDT Level III #48166
    The Snell Group
    www.thesnellgroup.com
    www.thermalsolutions.org
    800-636-9820
  •  06-29-2009, 10:27 PM 3196 in reply to 3195

    Re: 69kv Power Line Glowing

    Attachment: hotspot.JPG

    Great Catch it just reminds us all of how valuable our inspections are to all types of industries.

    Regards

    JK



    Jeremy Kays Reliability Technician
    Level II IR, MCA / UE Level I, In Compliance with the ASNT guidelines
    X-Ray Eyes
    xrayeyesjl@hotmail.com
    www.xrayeyesonline.com

  •  06-30-2009, 11:51 AM 3199 in reply to 3193

    Re: 69kv Power Line Glowing

    Justin,

     

    I've done some careful experiments to determine at what temperature an object begins to emit visual light. Using a totally darkened room, 4 different subjects first saw light emit from a electric coil at between 940F - 970F. Given the fact that it was not totally dark when you found the hot connection, I'd bet the surface temperature was easily over 1000F.

     Great find.

     Rob


    Rob Spring, P.E.
    ASNT NDT LIII #65375
    The Snell Group
    rspring@thesnellgroup.com
    800-636-9820
  •  07-01-2009, 5:41 PM 3206 in reply to 3199

    Re: 69kv Power Line Glowing

    Justin,

     Good story.  Sometimes we overlook the power of our own eyes as we proceed in our IR inspections and focusing on our camera displays.

    Rob,

     I concur with your temperature observations.  Back in my previous life in the gas patch, I came across some natural gas fueled, turbocharged engines in an enclosed building.  The turbocharger housings on the exhaust side were glowing red.  It was daytime but the building did not allow much sunlight.  Sensors on the engine exhaust stream indicated 1250 degrees, which was high but these engines were operating at over 105% capacity.  I would imagine the turbochargers experienced slightly lower temperatures and the outside of the housing was probably around 1100 degrees F.  This was before my IR days, but how many of us have cameras that can read 1100 degrees?

     Bill


    Bill Galbraith