2500KV Transformer 12470--480V

Last post 04-25-2008, 1:45 PM by Michael F Massman. 4 replies.
Sort Posts: Previous Next
  •  06-21-2007, 9:05 AM 303

    2500KV Transformer 12470--480V

    Attachment: ECC - 07 027.jpg
    Secondary bushing  inage attached, data below any coments?
     
    OAT 83 deg F           Start Time  1:20PM        Contact Temps at Tops of Bushing
    OIL --  Low      Oil Temp Start  114.8 F       Oil Temp Ending  120.2 F
    Unit  also has small oil leak welded seam top right front.
     
     
    TIME:                                         XO           X1            X2*          X3
     
                               AMPS                             354           354          354         
    1:20
                               TEMP F                          101           108          101
     
     
                               AMPS                             1293         1210        1245
    1:50 
                               TEMP F                          104           122          103
     
                              
                               AMPS               26         1254         1279         1234
    2:10
                               TEMP F                          107           131           106
     
    I advised Alan  to go back to the 4160V chillers and put as little 480V load on as possible until this anomaly is resolved. WO# 172896
     

    Thanks , 

     Think Thermally


  •  06-21-2007, 12:21 PM 305 in reply to 303

    Re: 2500KV Transformer 12470--480V

    Whilst the temperature level may not seem that high, I would be concerned about this. From the image it is difficult to tell exactly where the hottest point is, but it may be internal and could be some distance away. If this is the case, it will be a lot hotter. This, combined with the voltage would concern me very much. I would take an oil sample and get some DGA analysis ASAP and top up the oil.
    Bob Berry
    BINDT, IRT Level 3 EL, Level 3 CV
    Thermal Vision
    8 Old Fair Green
    Dunboyne
    Co Meath
    Ireland
    bob@thermalvision.ie
    www.thermalvision.ie
  •  06-22-2007, 1:35 AM 310 in reply to 303

    Re: 2500KV Transformer 12470--480V

    I'd concur that this is probably an internal fault and an advanced one. While a single data point of dissolved gas analysis (DGA) will not be very useful, it is probably useful to get one now in case you can't get to repairs soon and need to trend oil changes over time. Reducing and stabilizing loads would also be important. You don't want to let this one go and may want to suggest the customer schedule repairs at the next opportunity (certainly prior to critical summer loads). Keep us posted!
    Thermally Yours,

    John
    ASNT NDT Level III #48166
    The Snell Group
    www.thesnellgroup.com
    www.thermalsolutions.org
    800-636-9820
  •  06-22-2007, 7:58 PM 312 in reply to 303

    Re: 2500KV Transformer 12470--480V

    I thought that I would convert the image to colour as it may help with diagnostics.

     

     

     Definitely a problem. Good luck.


    Rory Paul
    Independent Level II Thermographer
    Barak Systems
    www.baraksystems.com
  •  04-25-2008, 1:45 PM 1416 in reply to 303

    Re: 2500KV Transformer 12470--480V

    UPDATE:

     Sorry for the long delay but the lead time on the new transformer and replacement took this long at least with reduced load it lasted long enough. After it was removed I took the top access cover off and could not see the connection I needed to probably because the oil was so dark smoky colored I could only see about 10" but it also took a week and a couple cleanings to get the burnt smell out of my jacket. To me the dark oil and the burnt smell physically confirms there was some kind of connection problem inside. Thanks for your help.