    utility pole

    Attachment: I0610-01.IMG
    I have 3 years as level I certified infrared thermographer, with most of my experience with electrical and mechinical on conveyor systems. I was going by a utility pole and noticed this one hot spot, there was almost no wind and it doesn't appear to be a reflection, I am hoping that someone can tell me whether or not this is a problem that needs to addressed
  •  06-10-2008, 5:28 AM 1530 in reply to 1529

    Re: utility pole

    Seems to be a broken link Bruce. Could you host it somewhere and insert it into a post?
  •  06-10-2008, 8:21 PM 1531 in reply to 1529

    Re: utility pole

    Attachment: I0610-01.IMG

    Let me try to post this picture again

     

     

  •  06-11-2008, 6:45 AM 1534 in reply to 1531

    Re: utility pole

    Hi folks,

     Since the image is in .IMG format, you will need to right click on the image link, and use "Save Target As" to store the image on your computer. Then you should be able to open it, assuming you have the proper software. Only the more garden variety image formats (JPEG, GIF, PNG, TIFF) will be displayed inline with your post.

    Best regards,


    Andrew Snell
    IRTalk.com System Administrator
    www.thesnellgroup.com
  •  06-11-2008, 9:59 PM 1540 in reply to 1531

    Re: utility pole

    Attachment: I0610-01.bmp

    I changed the file to a bitmap hopefully it can be accessed this time, I hope some will be able to tell me if this is actually a problem with this pole


  •  06-12-2008, 6:43 AM 1541 in reply to 1540

    Re: utility pole

    It looks like a problem.....it definately sticks out. Do you have a digital image of this?

    Jeff


    Jeff Gadd
    Vision Infrared Services
    www.visioninfrared.com
  •  06-12-2008, 7:31 PM 1544 in reply to 1541

    Re: utility pole

    Attachment: utility pole.bmp

    Here is the picture of the utility pole


  •  06-12-2008, 9:41 PM 1545 in reply to 1544

    Re: utility pole

    It looks like it may be a lightning arrestor which, if it is, should not be hotter than ambient. It is difficult to tell from the photograph. Is connected to a ground wire?
    Thermally Yours,

    John
    ASNT NDT Level III #48166
    The Snell Group
    www.thesnellgroup.com
    www.thermalsolutions.org
    800-636-9820
  •  06-12-2008, 11:17 PM 1546 in reply to 1545

    Re: utility pole

    Attachment: utility pole #2.JPG
    Yes, it has a ground wire attached to it
  •  06-13-2008, 6:21 AM 1547 in reply to 1546

    Re: utility pole

    It's looks like the arrester resistant is become lower than the other so it will cause heat inside the arrester. you may need another test such as insulation resistance test to confirm and compare with others. The arrester in your picture need to be inspected as soon as possible, because arrester is GO-NO-GO equipment, they don't have standard value to determine it is bad or still OK so you should replace them if heat sign is appear on them


    Sofan Afandi
    Electrical Technician
  •  06-16-2008, 5:05 AM 1554 in reply to 1547

    Re: utility pole

    It is difficult to say exactly from your photos, but I suggest you are looking at a lightning arrester that is failing. Any heat above ambient in these suggests impending failure which can occur catastrophically. I'd suggest you confirm your finding and consider scheduling replacement.

    I was invited to present a paper recently at the Doble conference on the topic of inspecting lightning arresters. If you, or other readers are interested, I can provide a copy to you. 


    Thermally Yours,

    John
    ASNT NDT Level III #48166
    The Snell Group
    www.thesnellgroup.com
    www.thermalsolutions.org
    800-636-9820
  •  06-16-2008, 8:30 PM 1555 in reply to 1554

    Re: utility pole

    Yes, I am interested in a copy of your paper could you email it to me at air1bjr@ups.com.

    Thank you

     

     Bruce J. Riopell

    Relability & Process Development Group
    Worldport Plant Engineering

    UPS Louisville, KY

  •  06-17-2008, 10:22 AM 1560 in reply to 1554

    Re: utility pole

    I also would like a copy. You can email me @ leow@fayette.coop

    Thanks in advance;

     