Dave,
I'd like to add to Johns comments.
I would not trust anyone using an infrared camera to compare window performance unless they first show an understanding of radiational physics as it applies to the infrared spectrum and competence in the use of an infrared imager.
Inspecting glass with an infrared imager presents a variety of potential pitfalls for the unaware (unconscious incompetent) thermographer. First, glass is spectral, meaning that its emissivity varies with wavelength. The emissivity in mid-wave is different than in longwave. Secondly glass is transmissive in wavelengths below 4.8 microns meaning that we are not only seeing radiation emitted from the surface but are seeing some radiation coming through the glass from the other side.
Most portable imagers being used today are long wave (8-14 microns). In long wave, uncoated window glass will have an emissivity somewhere from .8 to .9. Most of the samples I have tested are about .85. That means that glass is about 15 % to 20% reflective. Said another way, what you see is very dependent on what radiation is reflecting off the glass. As John mentioned above glass is also specular, allowing the thermographer to control what is reflecting off the surface by arranging the angle of view between the window, the background and the thermal imager. This allows a shyster (unscrupulous window salesperson) to play tricks with the IR camera. The old joke in IR thermography when playing with reflective materials is, “How hot would you like this to look?”
And as far as comparing one window to another to show relative thermal efficiency, that is job that can only be done in a controlled thermal environment. I'd stick to the reported R values on the window data sheet.
As the cost of IR imagers decreases and the number of untrained, inexperienced people using thermal imagers increases we will see more and more of these disturbing practices.
Rob Spring
Rob Spring, P.E.